四、1.3节“用电设备通过线缆进入室内连接到电源,是完整的供用电系统的末端器件,全然不是“孤立”的金属物。” 意见:GB50057-2010:4.5.7屋顶“孤立”金属物,“孤立”是林主编自己加上的,无非是说明“此屋顶金属物”与防雷装置,或者做为防雷装置的建筑物自然金属构件无直接联系而已。从IEC62305-2010E5.2.4.2.4看,屋顶电气装置如果和屋顶防雷装置无直接连接时,也属于屋顶“孤立”金属物。
E.5.2.4.2.4 Protection of flush-mounted orprotruding roof fixtures Air-termination rods for the protection of metal, flush-mounted rooffixtures or protruding roof fixtures should be of such height that the fixture to be protected liesfully within the rolling sphere protection space of the air-termination rod or is fully within thecone of the protection angle in accordance with Table 2. The separation distance between theair-termination rods and the roof fixtures should be such that the proximity conditionstipulated in 6.3 is satisfied. Figure E.29 shows an example of roof fixture protection by air-terminationrods using the protection angle air-termination design method. The value of theprotection angle shall be consistent with the protection level of the LPS stipulated in Table 2. Metal roof fixtures, not protected by air-termination rods, do not requireadditional protection if their dimensions do not exceed all of the following values: – height above the roof level 0,3 m; – the total area of the fixture 1,0 m2; – the length of the fixture 2,0 m. Metal flush mounted roof fixtures not fulfilling these requirements andnot being within the requirements forthe separation distance according to 6.3 IEC62305-2010 E.5.2.4.2.4 埋头安装或突出屋顶固定装置的防护
“对埋头安装的屋顶装置、突出屋顶装置提供保护的金属杆状接闪器,应安装在这样一个高度:受保护装置应完全处于杆状接闪器的滚球法保护空间内或完全处于表2的保护角的锥形保护区域内。杆状接闪器与屋顶装置的安全隔距应满足6.3的规定。
图E.29为一采用保护角法设计,由杆状接闪器为屋顶装置提供保护的例子。保护角的值应符合表2中LPS防护水平。
不在杆状接闪器保护范围内的金属屋顶固定装置,如果其尺寸不超过以下范围,则不需提供附加保护。
——高于屋顶平面上方0.3 m;
——固定装置总面积1.0 m2;
——固定装置的长度2.0 m。
埋头安装的金属屋顶固定装置不能达到这些要求,根据6.3隔距的要求,至少应用一根等电位连接导体与接闪器相等电位连接。”
上述前两段和E29的图说的就是屋顶电气装置的防雷做法,然后来了一个转折,如果其尺寸不超过以下范围,则不需。。。 所以,作者说用电设备不属于“孤立”金属物完全站不住脚。根本不是IEC标准的的意图。再说了,E5.2.4.2.4在IEC也只是个资料性附录,不具有和正文同等的效果。用一个推荐性的附录,提出设计中“不了解雷击机理”,“盲目和防雷装置连接”,就此整出一篇“防雷击研究”,是否合适? |