账号:
密码:
建筑电气
 找回密码
 我要注册
查看: 45349|回复: 107

IEC60364-5-54对“变电所中性点接地位置”的图示

   火.. [复制链接]
发表于 2011-1-6 12:32:50 | 显示全部楼层 |阅读模式

马上注册,结交更多好友,享用更多功能,让你轻松玩转社区。

您需要 登录 才可以下载或查看,没有账号?我要注册

×
《关于王厚余老师“变电所中性点不直接接地”提法的疑问?》一贴有些长了,我重开一贴,IEC最新标准的图示显示得很清楚。这些图在GB16895.3-2004中还没有。大家照此办理即可。
5-54-1a.JPG


5-54-1b.JPG

5-54-1c.JPG



5-54-a.JPG

C1  Water pipe, metal from outside  
C2  Waste water pipe, metal from outside
C3  Gas pipe with insulating insert, metal from outside
C4  Air-conditioning
C5  Heating system
C6  Water pipe, metal e.g. in a bathroom
C7  Waste water pipe, metal e.g. in a bathroom
D  Insulating insert
MDB  Main distribution board  
DB  Distribution board  
MET  Main earthing terminal
SEBT  Supplementary equipotential bonding terminal
T1  Concrete-embedded foundation earth electrode or soil-embedded foundation earth electrode
T2  Earth electrode for LPS if necessary
LPS  Lightning protection system (if any)
PE  PE terminal(s) in the distribution board
E/PEN  PE/PEN terminal(s) in the main distribution board
M  Exposed-conductive-part  
1  Protective earthing conductor (PE)
1a  Protective conductor, or PEN conductor, if any, from supplying network  
2  Protective bonding conductor for connection to the main earthing terminal
3  Protective bonding conductor for supplementary bonding  
4  Down conductor of a lightning protection system (LPS) if any
5  Earthing conductor

评分

参与人数 2E币 +40 收起 理由
尺短寸长 + 20 不奖不行!
gdx8785 + 20

查看全部评分

本帖被以下淘专辑推荐:

     
发表于 2011-1-6 12:41:57 | 显示全部楼层
热心人~{:42:}
发表于 2011-1-6 13:00:59 | 显示全部楼层
提示: 作者被禁止或删除 内容自动屏蔽
 楼主| 发表于 2011-1-6 13:08:00 | 显示全部楼层
[quote][/quote]回复 3# 治学以诚

无论在哪,变压器的PEN应先引入配电柜,再从配电柜中引出接地导电体接地,而不应在变压器处就近接地。
发表于 2011-1-6 13:47:25 | 显示全部楼层
提示: 作者被禁止或删除 内容自动屏蔽
     
发表于 2011-1-6 19:04:39 | 显示全部楼层
哪位兄弟解释解释这个图示。。。。

老诚,你行不。。。。
 楼主| 发表于 2011-1-7 09:34:23 | 显示全部楼层
本帖最后由 911room 于 2011-1-7 09:36 编辑

回复 6# 冷若冰

IEC60364-5-54原文是:
543.4.3  If, from any point of the installation, the neutral/mid-point/line and protective functions are provided by separate conductors, it is not permitted to connect the neutral/mid-point/line conductor to any other earthed part of the installation. However, it is permitted to form more than one neutral/mid-point/line conductor and more than one protective conductor from the PEN, PEL or PEM conductor respectively.  

The PEN, PEL or PEM conductor shall be connected to the terminal or bar intended for the
protective conductors (see Figure 54.1a), unless there is a specific terminal or bar intended for the connection of the PEN, PEL or PEM conductor (examples are given in Figures 54.1b and 54.1c).
 楼主| 发表于 2011-1-7 09:43:45 | 显示全部楼层
这段文字与现行GB16895.3-2004的描述没有区别,即:
543.4.3如果从装置的任一点起,中性导体和保护导体分别采用单独的导体,则不允许将该中性导体再连接到装置的任何其他的接地部分(例如,有PEN导体分接出的保护导体)。然而,允许有PEN导体分接出的保护导体和中性导体都超过一根以上。对保护导体和中性导体,可分别设置单独的端子或母线。在这种情况下,PEN导体应接到为保护导体预设的端子或母线上。

评分

参与人数 1贡献 +1 E币 +20 收起 理由
东海龙王 + 1 + 20 好图

查看全部评分

     
发表于 2011-1-8 13:06:36 | 显示全部楼层
本帖最后由 东海龙王 于 2011-1-8 09:13 编辑

人家图上已经标了MDB,老诚。
     
发表于 2011-1-8 13:13:58 | 显示全部楼层
本帖最后由 东海龙王 于 2011-1-8 09:48 编辑


1、题目改成“重复接地的图示”是不是更好?
2、既然引用IEC标准,仔细看看IEC TC64主席的关于低压系统接地的幻灯片。
     
发表于 2011-1-8 13:26:12 | 显示全部楼层
IEC TC64主席的幻灯片 在哪?
 楼主| 发表于 2011-1-10 10:11:40 | 显示全部楼层
回复 11# sccat
不知坛子里有没有,我知道在以下官网有:
http://tc64cn.org/user.asp
发表于 2011-1-10 10:39:17 | 显示全部楼层
结合专家提法个人观察:室外变压器带室内变电所,变压器处低压N点接地,变电所PEN线末端重复接地。如果是箱式变电站变压器低压N点与低压柜N排、PE排母线连接,只需一点接地。
发表于 2011-1-10 18:22:12 | 显示全部楼层
不知楼主是哪位高人,IEC还是没给出到底是N,PEN,还是PEN,PE。。。。。
     
发表于 2011-1-10 18:22:30 | 显示全部楼层
变压器处低压N点接地,变电所PEN线末端重复接地。———— 你这样是不是接地两次了。。。。
您需要登录后才可以回帖 登录 | 我要注册

本版积分规则