不如借鉴他山之石吧,NEC2011规定如下:(后面是原文,在下英文水平有限,翻译不妥之处请多包涵)
第210.52条(C)操作台插座布置
(C)台面。住宅的厨房、食品室、餐室及类似区域,台面区的电源插座应根据210.52(C)(1)至 (C)(5)要求进行安装。
(1)台面墙壁区。每面达到300mm或更宽的台面墙壁上应装1个插座。沿墙水平测量,任意点至插座间距不超过600mm。
例外:如图210.52(C)(1)所示,台面安装灶具和水盆正对的墙面上,不应安装插座。
(2)岛型台面区。每个达到600mm×300mm或更大面积的岛型台面区,至少应安装1个插座。
(3)半岛型台面区。沿连接边一侧测量,每个达到600mm×300mm或更大面积的半岛型台面区,至少应安装1个插座。
(4)分隔台面区。被灶具、冰箱或水盆分隔开的台面,应按210.52(C)(1)要求进行考虑。如果灶具或水盆安装于岛型或半岛型台面,灶具或水盆后面的台面进深小于300mm,则应将此台面分作两个台面进行考虑。每个分隔台面应分别满足210.52(C)要求。
(5)插座位置。插座应安装于台面表面或不超过500mm的上方。为家用电器配套的插座应允许安装在柜体内。因摆放电器、水盆、灶具等造成空间狭小,而使插座不便接近的情况,应作为210.52(C)(1)“例外”看待,不在此要求范围之内。
注:参见406.5(E)台面插座的安装要求
例外:为满足条款(1)或(2)的要求,插座应被允许安装在台面以下不超过300mm的位置回路。安装台面以下的插座不应超出台面支撑面150mm之外。
(1) 结构被削弱的情况
(2)在完整岛型和半岛型台面上(无挡板、隔断等),无法在高于台面500mm处,例如吊柜,安装插座的情况。
(C) Countertops. In kitchens, pantries, breakfast rooms, dining rooms, and similar areas of dwelling units, receptacle outlets for countertop spaces shall be installed in accordance with 210.52(C)(1) through (C)(5).
(1) Wall Countertop Spaces. A receptacle outlet shall be installed at each wall countertop space that is 300 mm (12 in.) or wider. Receptacle outlets shall be installed so that no point along the wall line is more than 600 mm (24 in.) measured horizontally from a receptacle outlet in that space.
Exception: Receptacle outlets shall not be required on a wall directly behind a range, counter-mounted cooking unit, or sink in the installation described in Figure 210.52(C)(1).
(2) Island Countertop Spaces. At least one receptacle shall be installed at each island countertop space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater.
(3) Peninsular Countertop Spaces. At least one receptacle outlet shall be installed at each peninsular countertop space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater. A peninsular countertop is measured from the connecting edge.
(4) Separate Spaces. Countertop spaces separated by range tops, refrigerators, or sinks shall be considered as separate countertop spaces in applying the requirements of 210.52(C)(1). If a range, counter-mounted cooking unit, or sink is installed in an island or peninsular countertop and the depth of the countertop behind the range, counter-mounted cooking unit, or sink is less than 300 mm (12 in.), the range, counter-mounted cooking unit, or sink shall be considered to divide the countertop space into two separate countertop spaces. Each separate countertop space shall comply with the applicable requirements in 210.52(C).
(5) Receptacle Outlet Location. Receptacle outlets shall be located on or above, but not more than 500 mm (20 in.) above, the countertop. Receptacle outlet assemblies listed for the application shall be permitted to be installed in countertops. Receptacle outlets rendered not readily accessible by appliances fastened in place, appliance garages, sinks, or range tops as covered in 210.52(C)(1), Exception, or appliances occupying dedicated space shall not be considered as these required outlets.
Informational Note: See 406.5(E) for requirements for installation of receptacles in countertops.
Exception to (5): To comply with the conditions specified in (1) or (2), receptacle outlets shall be permitted to be mounted not more than 300 mm (12 in.) below the counter-top. Receptacles mounted below a countertop in accordance with this exception shall not be located where the countertop extends more than 150 mm (6 in.) beyond its support base.
(1) Construction for the physically impaired
(2) On island and peninsular countertops where the countertop is flat across its entire surface (no backsplashes, dividers, etc.) and there are no means to mount a receptacle within 500 mm (20 in.) above the countertop, such as an overhead cabinet |