基于TOC法的某办公楼10 kV供电方案分析

来源于: 发表时间:2016-12-02 16:12 编辑:fzy

史泽刚 任   辉(唐山铭嘉建筑设计咨询有限公司,河北省唐山市 063000)

TOC - based Analysis of 10 kV Power Supply Scheme for an Office Building
SHI Zegang REN Hui(Tangshan Mingjia Architectural Design & Consulting Co.,Ltd.,Tangshan 063000,Hebei Province,China)
 
    Abstract:Consideration of the installation of high-capacity seasonal electrical loads to an office building in Tangshan City as well as the implementation of peak-valley TOU(time-of-use)price,several 10 kV power supply schemes are proposed for analysis. And the best 10 kV power supply scheme is determined by calculating and comparing the total owning cost(TOC)of transformer under the several schemes.
    Key words:peak-valley price;seasonal load;10 kV power supply scheme;TOC method;transformer;loss;annual charged hours;annual maximum load loss hours
 
    摘 要:针对唐山市某办公楼装设大容量季节性用电负荷且执行峰谷分时电价的特点,拟定几种10 kV供电方案进行分析,并通过计算比较几种供电方案变压器的综合能效费用(TOC),确定最佳的10 kV供电方案。
    关键词:峰谷电价;季节性负荷;10 kV供电方案;TOC法;变压器;损耗;年带电小时数;年最大负载损耗小时数
    中图分类号:TU852       文献标识码:A
     doi:10. 3969 / j. issn. 1003 - 8493. 2016. 11. 004