接触器长距离控制线路分析

来源于: 发表时间:2018-02-11 15:02 编辑:fzy

   凯 倪高俊(浙江大学建筑设计研究院有限公司,杭州市 310000)

Analysis on Long ?鄄 distance Control Circuit of Contactor
ZHENG Kai NI Gaojun(The Architectural Design & Research Institute of Zhejiang
University Co.,Ltd.,Hangzhou 310000,China)
 
    Abstract:Both the influence of long-distance control circuit voltage drop on the reliable switching -on of contactor and that of capacitance current between conductors on the reliable switching-off of contactor are analyzed. The maximum length of the allowable AC 220V control circuit for 2. 5 mm2 conductor satisfying the contactor switching-on and switching-off requirements is calculated by an example. The solution is proposed in case the maximum allowable length of control circuit cannot meet the engineering requirements.
    Key words:contactor;control circuit;switching-on power;retention power;intermediate relay;voltage drop;reliable switching-off of contactor;reliable switching-on of contactor
 
   摘 要:分析长距离控制线路电压降对接触器可靠吸合的影响,以及导线间电容电流对接触器可靠断开的影响,举例计算满足接触器吸合和断开要求的2. 5 mm2导线允许的AC 220V控制线路最大长度。提出当控制线路允许最大长度无法满足工程需求时的解决方案。
   关键词:接触器;控制回路;吸合功率;保持功率;中间继电器;电压降;接触器可靠断开;接触器可靠吸合
    中图分类号:TM572. 2        文献标识码:A