某商业综合体滑雪乐园配电系统可靠性分析

来源于: 发表时间:2018-05-04 16:05 编辑:fzy

贾云超 逄   京(北京市建筑设计研究院有限公司,北京市 100045)

Reliability Analysis on Power Distribution System of Skiing Park of a Commercial Complex
JIA Yunchao PANG Jing(Beijing Institute of Architectural Design Co.,Ltd.,Beijing 100045,China)
 
    Abstract:The evaluation indexes and the related algorithm for the reliability of the power distribution system are introduced briefly. The data analysis on the reliability of the power distribution system of the skiing park of a large commercial complex with ETAP electric power system analysis software is conducted,and the influence of the diesel generating set connected to the municipal power supply system on the reliability of the power distribution system and the influence of the different switching modes of diesel generators on the reliability of the power distribution system is discussed.
    Key words:commercial complex;recreation facility;power distribution system;distribution form;switching mode;power supply reliability;diesel generator;ETAP software
 
    摘 要:简介配电系统可靠性评估指标及相关算法。通过ETAP电力系统分析软件对某大型商业综合体滑雪乐园项目配电系统的可靠性进行数据分析,探讨市政供电系统中接入柴油发电机组对配电系统可靠性的影响以及柴油发电机不同的投切方式对配电系统可靠性的影响。
    关键词:商业综合体;游乐设施;配电系统;配电形式;投切方式;供电可靠性;柴油发电机;ETAP软件