高层建筑火灾自动报警系统电压损失研究

来源于: 发表时间:2018-06-01 16:06 编辑:fzy

张仁红(中国建筑西南设计研究院有限公司贵州分院,贵阳市 550001)

Research on Voltage Losses of Automatic Fire Alarm Systems in High - rise Buildings
ZHANG Renhong(Guizhou Branch of China Southwest Architectural Design and Research Institute Corp. Ltd,Guiyang 550001,China)
 
    Abstract:The significance and current situation of the automatic fire alarm systems used in the fast-developing high-rise buildings are introduced briefly,and the influence of the voltage loss on the automatic fire alarm system is proposed. Meanwhile,the main factors for the voltage loss on the power line of the automatic fire alarm system are analyzed,and the measure to choose the power line more reasonably at different power supply distances is summarized by calculating and deducing the voltage losses of the automatic fire alarm systems in the high-rise residences,in order to provide the reliable circuit guarantee for the automatic fire alarm system.
    Key words:high-rise buildings;voltage loss;power line;automatic fire alarm system;cross-section of conductor;calculating current;voltage deviation;power supply distance
 
    摘 要:简述目前火灾自动报警系统在高速发展的高层建筑中运用的重要性与现状,提出电压损失对火灾自动报警系统的影响。同时,分析火灾自动报警系统中导致电源线路上电压损失的主要因素,并以高层住宅的火灾自动报警系统为例,通过对其电源线路上电压损失的计算和推导,得出在不同供电距离下,怎样更合理地选择电源线,为火灾自动报警系统提供可靠的线路保障。
    关键词:高层建筑;电压损失;电源线;火灾自动报警系统;导线截面;计算电流;电压偏差;供电距离