也谈等电位联结

来源于: 发表时间:2018-08-22 15:08 编辑:fzy

丁 杰(中国航空规划设计研究总院有限公司,北京市 100120)

陈 谦(山东意匠建筑设计有限公司,济南市 250022)
韩 帅(天津市天友建筑设计股份有限公司,天津市 300384)
Further Discussion about Equipotential Bonding
DING Jie(China Aviation Planning and Design Institute(Group)Co.,Ltd.,Beijing 100120,China)
CHEN Qian(Shandong Yijiang Architectural Design Co.,Ltd.,Ji’nan 250022,China)
HAN Shuai(Tenio Tianjin Architecture and Engineering Co., Ltd.,Tianjin 300384,China)
 
    Abstract:The necessity of protecting equipotential bonding is emphasized through the analysis of the damage of high and low voltage erath faults to TN system;setting local equipotential bonding at regional distribution box can play a function of effective additional protection. With the development of standards,local equipotential bonding and supplementary equipotential bonding in IEC have achieved integration,and China’s standards shall be well coordinated and unified with relevant standards.
    Key words:earth fault;multiple grounding;additional protection;supplementary equipotential bonding;local equipotential bonding;automatic power cut-off;extraneous conductive parts;prospective touch voltage
 
    摘 要:通过对TN系统高、低压接地故障危害的分析,强调保护等电位联结的必要性;在区域配电箱处设置局部等电位联结能起到有效的附加防护功能;随着标准的发展,IEC中局部等电位联结和辅助等电位联结实现了融合,我国标准应做好相关标准之间的协调统一。
    关键词:接地故障;重复接地;附加防护;辅助等电位联结;局部等电位联结;自动切断电源;装置外可导电部分;预期接触电压
     中图分类号:TU899               文献标识码:A
     doi:10. 3969 / j. issn. 1003 - 8493. 2018. 08. 002