中性导体断线故障防护分析

来源于: 发表时间:2019-01-09 17:01 编辑:fzy

陈 谦(山东意匠建筑设计有限公司,济南市 250022)

韩 帅(天津市天友建筑设计股份有限公司,天津市 300384)
谢 炜(苏州一科科建建筑设计研究院有限公司,江苏省苏州市 215006)
Analysis on Fault Protection of Neutral Conductor Disconnection
CHEN Qian(Shandong Yijiang Architecture Design Co.,Ltd.,Ji’nan 250022,China)
HAN Shuai(Tianjin TENIO Architecture and Engineering Co.,Ltd.,Tianjin 300384,China)
XIE Wei(Suzhou Yike Kejian Architectural Design & Research Institute
Co.,Ltd.,Suzhou 215006,Jiangsu Province,China)
 
 
    Abstract:The problem of neutral conductor disconnection fault is discussed,and the issues about safety in application of the overvoltage and undervoltage protective device are analyzed. Moreover,European product standards and test points for similar purposes are introduced,with a view to achieving the coordination between protection trip and undesired interruption of power supply,indicating that the European Committee for Electrotechnical Standardisation(CENELEC)and International Electrotechnical Commission (IEC)put emphasis on the protection of neutral conductor disconnection faults in households and similar places.
    Key words:neutral conductor disconnection;fault voltage protective device;overvoltage and undervoltage protective device;power frequency overvoltage protective device;tripping curve;reclose mechanism;insulation coordination;temporary overvoltage
 
    摘 要:对中性导体断线故障问题展开讨论,就过欠电压保护器应用中的安全问题进行分析。介绍欧洲类似用途的产品标准及试验要点,重点做到保护跳闸和不期望中断供电之间协调统一,表明欧洲电工标准化委员会和国际电工委员会(IEC)对家用及类似场所中性导体断线故障保护的重视。
    关键词:中性导体断线;故障电压动作保护器;过欠电压保护器;工频过电压保护器;跳闸曲线;自恢复机制;绝缘配合;暂时过电压
     中图分类号:TM773               文献标识码:A
     doi:10. 3969 / j. issn. 1003 - 8493. 2018. 12. 001