《数据中心工程设计与安装》要点解读

来源于: 发表时间:2019-01-17 17:01 编辑:fzy

 

钟景华(中国电子工程设计院有限公司,北京市 100142

Analysis on Gist of the Engineering Design and Installation of Data Centers

ZHONG JinghuaChina Electronics Engineering Design Institute Co.Ltd.Beijing 100142China

 

    AbstractIn this paper, an analysis is made on the gist of the national building standards design atlas 18DX009 Engineering Design and Installation of Data Centerswith the aim to interpret the requirements for equipment layoutpower supply and distributiontemperaturedew point temperature and relative humidity. The equipment layout involves personnel safetyventilation and heat dissipationequipment transportation and maintenancethe power supply and distribution involve a basic performance requirement and two expansibility requirements of a Class A data centerand the temperaturedew point temperature and relative humidity are the basic parameters for the air conditioning design of a data center.

    Key wordsnational building standards design atlasdata centerequipment layoutevacuation exitpower supply and distributiondedicated feeder linediesel generator unittemperaturedew point temperature and relative humidity

 

    摘 要:解读国家建筑标准设计图集18DX009《数据中心工程设计与安装》要点,理解设备布置、供配电及温度、露点温度和相对湿度等要求。设备布置涉及人员安全、通风散热、设备运输和维护等;供配电涉及A级数据中心的一个基本性能要求和两个扩展性能要求;温度、露点温度和相对湿度是数据中心空调设计的基本参数。

    关键词:国家建筑标准设计图集;数据中心;设备布置;疏散通道;供配电;专用馈电线路;柴油发电机组;温度、露点温度和相对湿度

     中图分类号:TU202              文献标识码:A

     doi10. 3969 / j. issn. 1003 - 8493. 2019. 01. 001