NOTE 1 Examples of conditions include:
− the PEN is connected to earth at a number of points and is installed in such a way as to minimize the risk of a
break in the PEN conductor;
− RB/RE ≤ 50/(U0 – 50)
where
RB is the earth electrode resistance, in ohms, of all earth electrodes in parallel;
RE is the minimum contact resistance with earth, in ohms, of extraneous-conductive-parts not connected to a
protective conductor, through which a fault between line and earth may occur;
Uo is the nominal a.c. r.m.s. voltage to earth, in volts.
NOTE 2 In Germany compliance with condition RB/RE ≤ 50 / (Uo – 50) is compulsory for the supply network
operator. |
|