商业综合体建筑电气负荷密度研究

来源于: 发表时间:2021-06-07 19:06 编辑:fzy

 

商业综合体建筑电气负荷密度研究

李炳华(悉地国际集团,北京市 100013

   岳云涛    昊(北京建筑大学,北京市 100044

 

Study on Electrical Load Density of Commercial Complex Buildings

LI BinghuaCCDI Group,Beijing 100013China

PAN Xin YUE Yuntao CHANG Hao

Beijing University of Civil Engineering and Architecture,Beijing 100044China

 

 

AbstractAccording to the characteristics of commercial complex buildings,through investigation on the actual installed capacity of a large number of commercial complex buildings,the characteristics of commercial complex buildings are analyzed and compared from the perspective of electrical load density,and the influence of super highrise buildings and thermal zoning on commercial complex buildings is obtained. Bootstrap method is used to analyze and obtain the TCPA and the recommended values of power,airconditioning and lighting load density selection range,which can provide reference for the electrical scheme design of commercial complex buildings.

Key wordscommercial complex building;TCPA;load density;Bootstrap method;confidence interval;power load;airconditioning load;lighting load

 

摘 要:针对商业综合体建筑的特点,通过调研大量商业综合体建筑实际安装容量,从电气负荷密度的角度来分析比较商业综合体建筑的特点,得出超高层及热工分区对商业综合体建筑的影响。利用Bootstrap法分析得到变压器容量指标和动力、空调、照明负荷密度选取范围建议值,对商业综合体建筑电气方案设计提供参考。

关键词:商业综合体建筑;变压器容量指标;负荷密度;Bootstrap法;置信区间;动力负荷;空调负荷;照明负荷