额定功率小于25 W的LED灯具谐波含量探讨
陈钟毓(北京市建筑设计研究院有限公司,北京市 100045)
Discussion on Harmonic Content of LED Luminaire With the Rated Power of Less than 25 W
CHEN Zhongyu(Beijing Institute of Architectural Design(Group)Co.,Ltd.,Beijing 100045,China)
Abstract:This paper measures the harmonic content of 18 various types of LED luminaires,and determines the limit of total harmonic distortion (THD)according to the Electromagnetic Compatibility (EMC)— Part 3 - 2: Limits — Limits for Harmonic Current Emissions(Equipment Input Current ≤ 16 A per Phase(IEC 61000 - 3 - 2:2018). It also compares the harmonic content of various types of LED luminaires under the dimming state,and analyzes the measurement results.
Key words:LED luminaire; harmonic wave;total harmonic distortion(THD);power factor;full power factor;electrical parameters;comparative analysis;electrical energy saving
摘 要:对18款不同类型LED灯具的谐波含量进行测量,依据IEC 61000-3-2:2018《 Electromagnetic compatibility(EMC)— Part 3 - 2:Limits — Limits for harmonic current emissions (equipment input current ≤ 16 A per phase)》对灯具总谐波畸变率(THD)限值进行判定。同时对比不同类型LED灯具在调光状态下的谐波含量,并对测量结果进行分析。
关键词:LED灯具;谐波;总谐波畸变率(THD);功率因数;全功率因数;电参数;对比分析;电气节能
中图分类号:TM923.34 文献标识码:A
doi:10.3969 / j. issn.1003 - 8493.2022.02.009