疏散照明中均布负荷的电压损失计算
张俊明(北京城建设计发展集团股份有限公司,北京市 100037)
Calculation of Voltage Loss for Uniform Loads in Emergency Lighting
ZHANG Junming(Beijing Urban Construction Design & Development
Group Co.,Limited,Beijing 100037,China)
Abstract:The uniform loads in emergency lighting are converted into concentrated loads to calculate the voltage loss and derive the formula;then,the longest converted distribution distance is determined for different wire specifications upon the maximum voltage loss according to the formula;and it is simulated to determine the distribution scheme for emergency lighting in subway sections.
Key words:emergency lighting;concentrated load;uniform load;voltage loss calculation;power distribution distance;centralized power supply;formula derivation;scheme simulation
摘 要:将疏散照明中的均布负荷折算为集中负荷后进行电压损失计算,并导出公式;依据公式确定不同导线规格在达到最大电压损失时,最长的折算配电距离;模拟确定地铁区间疏散照明的配电方案。
关键词:疏散照明;集中负荷;均布负荷;电压损失计算;配电距离;集中电源;公式推导;方案模拟
中图分类号:TU852 文献标识码:A
doi:10.3969 / j. issn.1003 - 8493.2023.06.010