基于航班信息的照明节能控制技术研究

来源于: 发表时间:2024-11-28 11:11 编辑:fzy

 

   崔明丽 张文武 钟世权(广东省建筑设计研究院集团股份有限公司,广州市 510010

赵骥   崔明丽   张文武   钟世权

Research on Flight Information‑based Lighting Energy Saving Control Technology

ZHAO Ji CUI Mingli ZHANG Wenwu ZHONG Shiquan

(Guangdong Architectural Design and Research Institute Group Co.,Ltd.,Guangzhou 510010China)

 

 

AbstractIn this paper,taking the lighting control of an airport terminal as an example,a method is proposed in which the number of passengers is predicted based on flight information,and accordingly the lighting partition is divided,the passenger density is calculated,the standard value of illuminance is calibrated,and then the method of linkage control of the lighting system at different levels is realized. This method optimizes the operation of the lighting system while ensuring the safety and comfort of passengers and also significantly reduces energy consumption.

Key wordsintelligent lighting control;lighting partition;flight information;predicted number of passengers;passenger density;flight linkage mode;lighting control at different levels;standard value of illuminance

 

摘 要:结合某机场航站楼照明控制设计实际案例,提出基于航班信息预测旅客数,并据此划分照明分区、计算旅客密度、校验照度标准值,进而联动照明系统分档位控制的方法,在保证旅客安全和舒适度的同时,优化照明系统的运行方式,也较大幅度降低能耗。

关键词:智能照明控制;照明分区;航班信息;预测旅客数;旅客密度;航班联动模式;照明分档位控制;照度标准值

中图分类号:TU88                     文献标识码:A

doi10.3969 / j. issn.1003 8493.2024.10.010