账号:
密码:
    QQ登录
建筑电气
当前位置:首页 >> 建筑电气杂志 >> 2009年第06期(总第139期)

某银行计算机中心电气故障解决案例

来源于: 发表时间:2010-01-12 17:01 编辑:系统管理员

程绍颐(甘肃省建筑设计研究院,兰州市 730030)

冯志文(陕西省建筑设计研究院有限责任公司,西安市 710003)
 
Solution Case for the Electrical Fault in a Bank Computer Center
Cheng Shaoyi(Gansu Institute of Architectural Design & Research,Lanzhou 730030,China)
Feng Zhiwen(Shanxi Architectural Design & Research Institute Co.,Ltd.,Xi’an 710003,China)
 
Abstract The analysis process and solutions for the electrical fault in a bank computer center are introduced. UPS switch along with the external protection switch tripped many times because of fault,the causes of which are that:① the N conductor and the PE conductor in the TN-C-S system are first separated and then combined;② three-phase load is unbalanced;③ harmonic impact.
Key words Electrical fault Grounding Three-phase load unbalance Voltage between N conductor and ground Neutral point offset Harmonics
 
摘 要 介绍了某银行计算机中心电气故障的分析过程和解决措施。UPS 保护开关连同外部保护开关多次发生故障跳闸,分析其原因为:① TN - C - S 系统中 N 线与 PE 线分开后又合并;② 三相负荷不平衡;③ 谐波影响。
关键词 电气故障 接地 三相负荷不平衡 N线对地电压 中性点偏移 谐波

相关信息:

  • 推荐文章

  • 热门文章