谈谈走廊和楼梯间的照明设计

来源于: 发表时间:2010-04-07 12:04 编辑:付泽艺

余悦兰(国立华侨大学建筑设计院,福建省泉州市 362021)

Discussion about the Lighting Design for Corridors and Staircases
Yu Yuelan(Architectural Design Institute,National Huaqiao University,Quanzhou 362021,Fujian Province,China)
Abstract Taking lighting layout modes commonly used in the engineering design as an example, using point illuminance calculation method, the illuminance of normal lighting and emergency lighting in the corridors and staircases are calculated in details. The results show that the lighting design methods that have been widely used in engineering design cannot meet the illuminance requirements for the corridors and staircases stipulated in the existing code;and the illuminance of the emergency lighting cannot meet the requirements of the relevant compulsory article.
Key words Corridor Staircase Illuminance Emergency lighting
摘 要 以工程设计中常用的布灯方式为例,采用点照度计算法详细计算了走廊和楼梯间正常照明和应急照明的照度。结果表明,工程设计中广泛采用的照明设计方式不能满足现行规范对走廊和楼梯间的照度要求,应急照明的照度也不能满足有关强制性条文的要求。
关键词 走廊 楼梯间 照度 应急照明