杨 泓 高 峰 杜淑文(中建国际(深圳)设计顾问有限公司,上海市 200433)
Comparative Analysis of 35 kV Power Transformation and Distribution
Schemes for Ultra-large Buildings
Yang Hong Gao Feng Du Shuwen(China Construction Design International,Shanghai 200433,China)
Abstract Taking a project as an example,a technical and economic comparison between 35 / 0 .4 kV and 35 / 10 / 0.4 kV power transformation and distribution schemes for ultra-large buildings substations are made on several aspects, such as the major equipment investment,floor area,power consumption and so on,the project has finally adopted a 35 / 10 / 0.4 kV two -stage power transformation scheme.
Key words Ultra -large building Extra -high
building 35 / 0 .4 kV one - stage power transformation
35 / 10 / 0.4 kV two - stage power transformation Equipment investment F loor area Power consumption
摘 要 以某工程项目为例,对超大型建筑群 35 / 0 .4 kV 和 35 / 10 / 0 .4 kV 两种变配电方案的主要设备投资、占地面积、电能损耗等几方面进行了技术经济比较,该项目最终采用了 35 / 10 / 0 .4 kV 二级变电方案。
关键词 超大型建筑 超高层建筑 35 / 0 .4 kV一级变电 35 / 10 / 0 .4 kV 二级变电 设备投资 占地面积 电能损耗