Fault Analysis of a Relay Protection Override Trip and Discussion on the Relay Protection Selectivity
Chen Ruzhong(Xiamen International Airport Co.,Ltd.,Xiamen 361006,Fujian Province,China)
Abstract A large current short -circuit fault occurred in the low -voltage bus-tie switch cabinet at the substation of a central machinery factory,which led to the simultaneous override trip of the two stages of high -voltage circuit breaker of the superior 10 kV distribution substation. Analysis is conducted directing at the phenomena,reason,relay protection settings,and protection action value of this fault;meanwhile high -voltage relay protection is expounded;based on these,the paper comes to the conclusion that it is necessary and important to set gradation for relay protection actuation time and current start value in high -voltage distribution system including multi -grade substations.
Key words Bus-tie switch Override trip Relay protection Protection selection
摘 要 某中心机械厂变配电所低压母联开关柜发生大电流短路故障,导致上级 10 kV 配电所的两级高压断路器同时越级跳闸,针对这次故障的现象、原因、继保整定值、保护动作值进行分析,同时对高压继电保护进行阐述,得出在包含多级子站的高压配电系统中,继电保护动作时间及电流启动值设置级差的必要性与重要性。
关键词 母联开关 越级跳闸 继电保护 保护选择