Technique Analysis for IP Errors for Automatic Comprehensive Monitoring System
of Transformer Substation
Cui Yong(North China Electric Power University,Beijing 102206,China)
Wang Chuan(Jiangxi Ji’an Power Supply Co.,Ltd.,Ji’an 343000,Jiangxi Province,China)
Chen Xianghua(Qinghai Xining Fangsheng Electrical Power Designing Co.,Ltd.,Xining 810003,China)
Zhu Bao(Wuhan Fiberhome Fuhua Electric Co.,Ltd,Wuhan 430074,China)
作者信息
崔 勇,男,华北电力大学,工程师,博士研究生。
王 川,男,江西吉安供电公司,助理工程师,值班长。
陈湘华,男,青海西宁方盛电力设计有限公司,工程师。
朱 宝,男,武汉烽火富华电气有限公司,助理工程师。
Abstract Both measuring & control devices or protectors of the automatic comprehensive monitoring system of transformer substation have their own exclusive IP address. IP address overlap(if any)will definitely result in simultaneous implementation of instructions. This paper makes conclusions by analyzing accident case and suggests precautionary measures for some measuring and control devices manufacturers which fail to set address overlap or error identification function for their products.
Key words Automatic comprehensive monitoring system IP address Instruction identification
摘 要 变电站综合监控自动化系统中测控或保护装置均有专属 IP 地址,如果发生地址重复必然导致指令目标的同时执行。通过事故案例的分析得出结论。针对目前部分测控装置生产厂家未设置地址重复或错误识别功能,提出防范措施。
关键词 综合监控自动化系统 IP 地址 指令识别