世博会庆典广场喷泉变配电所谐波抑制

来源于: 发表时间:2012-02-08 14:02 编辑:fzy

邵 頲(现代建筑设计集团工程建设咨询有限公司,上海市 200070)

Harmonic Suppression of Distribution Substation for Fountain on the Celebration Plaza during Shanghai World Expo
Shao Ting(Engineering & Construction Consulting Co., Ltd.,Shanghai Xian Dai Architectural Design(Group)Co.,Ltd.,Shanghai 200070,China)
 
    Abstract The load characteristics of the distribution substation for fountain on the Celebration Plaza during Shanghai World Expo are analyzed,and the harmonic suppression and treatment scheme for mutational nonlinear equipment with large capacity are discussed. Based on the statistical data of harmonic test of such load, the harmonic current is estimated,the active power filter is designed and selected,and the harmonic data before and after the application of the active power filter are analyzed by comparison.
    Key words Nonlinear load Harmonic characte ?ristics Frequency conversion equipment Dimmer device Active power filter Power supply and distribution environment
 
    摘 要 分析世博会庆典广场喷泉变配电所负荷特征,探讨大容量、突变性非线性设备的谐波抑制和治理方案。依据该类型负荷谐波测试统计数据,估算谐波电流,设计选用有源电力滤波器,并对比分析有源电力滤波器投入前后的谐波数据。
    关键词 非线性负荷 谐波特征 变频设备 调光装置 有源电力滤波器 供配电环境