低压电缆耐火试验国标和英标的差异分析

来源于: 发表时间:2012-03-29 15:03 编辑:fzy

陈杰甫(上海建筑设计研究院有限公司,上海市 200041)

余维科(上海高桥电缆集团有限公司,上海市 201605)
Analysis on Difference between National Standards and British Standards for Fire-resistant Test of Low-voltage Cable
Chen Jiefu(Shanghai Institute of Architectural Design & Research(Co.,Ltd),Shanghai 200041,China)
Yu Weike(Shanghai SHGQ Cable Group Co.,Ltd,Shanghai 201605,China)
 
   
Abstract On the basis of the comparison of difference between the national standards for fire - resistant test of low - voltage cable,GB 19216. 21 - 2003 / IEC 60331 - 21:1999 Tests for Electric Cables under Fire Conditions — Circuit integrity — Part 21:Procedures and Requirements — Cables of Rated Voltage up to and Including 0. 6 / 1. 0 kV,and British standard BS 6387:1994 Specification for Performance requirements for cables required to maintain circuit integrity under fire conditions,the standpoints,test content and methods are analyzed;after the comparison and analysis of the difference,the test content of BS 6387:1994 is introduced in detail,so as to provide reference for designers to understand the difference between the two standards.
Key words Fire - resistance test for cable Fire -resistant cable Standards difference
 
摘 要 通过对比低压电缆耐火试验国家标准GB 19216. 21 - 2003 / IEC 60331 - 21:1999《在火焰条件下电缆或光缆的线路完整性试验 第21部分: 试验步骤和要求 额定电压0. 6 / 1. 0 kV及以下电缆》和英国标准BS 6387:1994《Specification for Performance requirements for cables required to maintain circuit integrity under fire conditions》的差异,分析两个标准制订的出发点、试验内容和试验方法。对比分析存在的差异性,并详细介绍BS 6387:1994的试验内容,为设计人员了解两个标准的差别提供参考。
关键词 电缆耐火试验 耐火电缆 标准差异