Application of Active Power Filter to Data Center
Liu Xiaofang(Shanghai Institute of Architectural Design & Research Co.,Ltd.,Shanghai 200041,China)
Abstract Burning out of capacitance compensation cabinet and trip failure of main breaker of low-voltage cabinet have happened for several times in the substation of a data center which has been put into operation. According to the field investigation,it is believed that the electric failures may be caused from excessive UPS configuration for the terminal computer,and harmonic pollution caused from using of a large number of LED lights. Effect of application of active power filter to the data center is introduced on the basis of field measurement of the harmonic data before and after setting of active power filter.
Key words Active power filter Harmonic suppression Data center