直流微网中平行DC / DC变换器的控制

来源于: 发表时间:2016-03-18 11:03 编辑:fzy

叶友泉 杨冠鲁(华侨大学,福建省厦门市 361021)

Control of Parallel DC / DC Converters in DC Microgrid
YE Youquan YANG Guanlu(Huaqiao University,Xiamen 361021,Fujian Province,China)
 
 
Abstract:This article proposes a photovoltaic (PV)DC microgrid system which employs multi-wall PV. In the DC microgrid,the droop control strategy widely used in parallel control of inverter is adopted for the control of parallel DC / DC converters,forming a triple-loop control together with voltage and current loops,which restrains the loop current between parallel DC / DC converters. Simulink simulation shows that,stable DC bus voltage and effective control over the loop current among parallel DC / DC converters can be achieved by this way. In the end,an experimental platform is built in the lab to verify the feasibility of this control strategy
Key words:photovoltaic DC microgrid;DC / DC converter;DC bus voltage;droop control;virtual impedance;loop current;triple-loop control strategy;simulation
 
    摘 要:提出以多墙体光伏为研究对象的光伏直流微网系统。将在逆变器并联控制中广泛使用的下垂控制策略应用到平行DC / DC变换器的控制中,与电压、电流环构成三闭环控制,从而抑制平行DC / DC变换器之间的环流。通过Simulink仿真分析,该方法能够实现直流母线电压的稳定及有效抑制各平行DC / DC变换器之间的环流。最后,在实验室搭建实验平台,验证该控制策略的可行性。
    关键词:光伏直流微网;DC / DC变换器;直流母线电压;下垂控制;虚拟阻抗;环流;三闭环控制策略;仿真
    中图分类号:TM615       文献标识码:A
     doi:10. 3969 / j. issn. 1003 - 8493. 2016. 03. 008