Research on Dynamic Switching of Operation Mode of Spray Pump in Multiple Fire Compartments
JIANG Changfa(Zhengzhou University Multi-functional Design and Research Academy
Co.,Ltd.,Zhengzhou 450000,China)
JIANG Bo(Yellow River Engineering Consulting Co.,Ltd.,Zhengzhou 450000,China)
Abstract:An improved control schematic diagram of the water pump is proposed for the design of the spray system of an actual underground garage. When a fire alarm occurs in the mechanical garage,three pumps operate in the state of two in use and one on standby. When the fire alarm occurs in an ordinary garage,they can be automatically converted to the operating state of one in use and one on standby.
Key words:automatic spray pump;two in use and one on standby;one in use and one on standby;wet alarm valve pressure switch;operation mode;control schematic diagram;operating state switching;fire compartment
摘 要:针对某实际地下车库喷淋系统设计,提出一种改进后的水泵控制原理图:当机械车库发生火灾报警时3台水泵按照两用一备状态运行;当火灾报警为普通车库时能够自动转换为一用一备运行状态。
关键词:自动喷淋泵;两用一备;一用一备;湿式报警阀压力开关;运行方式;控制原理图;运行状态切换;防火分区