陈 技 林洪钟 黄园梅(福建省建筑设计研究院有限公司, 福州市 350001)
Discussion on Some Problems of Automatic Fire Alarm System Design
CHEN Ji LIN Hongzhong HUANG Yuanmei
(Fujian Provincial Institute of Architectural Design and Research Co.,Ltd.,Fuzhou 350001,China)
Abstract:In accordance with the Code for Design of Automatic Fire Alarm System(GB 50116 - 2013)and relevant local regulations,the issues related to the selection of alarm system type and equipment layout,system design at special parts of buildings,and settings of collection point of monitoring on power distribution system of firefighting apparatus are discussed with suggestions given by the author. Solutions are proposed for the implementation of overlooked provisions in the specification and issues not covered by the specific works.
Key words:fire control room;detector;fire-fighting water pump house;power monitoring;smoke-proof and exhaust fan room;deluge valves unit;fire control module;double power mutual switching
摘 要:结合国家标准GB 50116 - 2013《火灾自动报警系统设计规范》及相关地方规定,探讨火灾自动报警系统形式的选择、设备的设置、建筑物特殊部位火灾自动报警系统设计、消防设备配电系统电源监控采集点的设置等问题,并给出作者的建议。对规范在建筑电气设计中如何贯彻、容易忽略的条文,以及具体工程项目中规范未涉及的问题,提出相应的解决方案。
关键词:消防控制室;探测器;消防水泵房;电源监视;防排烟风机房;雨淋阀组;消防模块;双电源互投
中图分类号:TU892 文献标识码:A
doi:10. 3969 / j. issn. 1003 - 8493. 2019. 10. 008