李国会 张 晶(中国建筑西南设计研究院有限公司,成都市 610042)
GB 51309 - 2018对民用建筑非应急照明设计的影响(李国会 张晶)
Impacts of GB 51309 - 2018 on Non‑emergency Lighting Design
LI Guohui ZHANG Jing(China Southwest Architectural Design and Research Institute
Corp. Ltd.,Chengdu 610042,China)
Abstract:The impacts of GB 51309 - 2018 on the power supply and control requirements for non‑emergency lighting in typical places garage,above‑ground aisles and stairwell in the buildings are analyzed by comparing the new provisions of GB 51309 - 2018 Technical Standard for Fire Emergency Lighting and Evacuate Indicating System with the traditional practice,and relevant design suggestions are given from the perspective of practical use and energy conservation.
Key words:central controlled fire emergency lighting system;non‑emergency lighting;garage lighting;aisle lighting;stairwell lighting;stand‑by power supply;lighting control;energy conservation
摘 要:对比GB 51309 - 2018 《消防应急照明和疏散指示系统技术标准》的新规定与传统做法的不同,分析GB 51309 - 2018对建筑内的典型场所车库、地上走道、楼梯间非应急照明的供电、控制要求的影响,从实际使用、节能角度给出设计建议。
关键词:集中控制型应急照明系统;非应急照明;车库照明;走道照明;楼梯间照明;备用电源;照明控制;节能