中压电缆的热稳定校验
焦建雷(北京兴电国际工程管理有限公司,北京市 100048)
中压电缆的热稳定校验(焦建雷)
Thermal Stability Verification of Medium‑voltage Cables
JIAO Jianlei(Beijing Scientech International Project Management Co.,Ltd.,Beijing 100048,China)
Abstract:According to the short‑circuit current,cable specification and length of the 10 ~ 20 kV busbar of the substation in the grid area,the short‑circuit current of medium‑voltage cables are calculated by the Short‑circuit Current Calculation in Three‑Phase a.c. Systems(GB / T 15544 / IEC 6090),and short‑circuit thermal stability is verified based on the time of relay protection action;the application of short circuit thermal stability verification form of medium‑voltage cables in the national standard atlas 19DX101 - 1 Common Data of Building Electricity are validated and illustrated.
Key words:short‑circuit current;GB / T 15544(IEC method);medium‑voltage cable;cable specification;action time;thermal stability verification;calculation formula;national standard atlas
摘 要:根据电网区域变电站10 ~ 20 kV母线的短路电流、电缆规格及长度,用GB / T 15544 / IEC 6090系列标准《三相交流系统短路电流计算》计算中压电缆短路电流,根据继电保护动作时间来校验短路热稳定;并对国标图集19DX101 - 1《建筑电气常用数据》中中压电缆短路热稳定校验表格的应用进行验证和说明。
关键词:短路电流;GB / T 15544(IEC法);中压电缆;电缆规格;动作时间;热稳定校验;计算公式;国标图集
中图分类号:TU852 文献标识码:A
doi:10.3969 / j. issn.1003 - 8493.2021.02.012