对防火阀、排烟防火阀设置的思考
陈志萍(山西省建筑设计研究院有限公司,太原市 030013)
Thoughts on Setting of Fire Damper and Smoke Exhaust Fire Damper
CHEN Zhiping(Shanxi Architectural Design and Research Institute Co.,Ltd.,Taiyuan 030013,China)
Abstract:The regulations on various fire dampers,smoke exhaust fire dampers,and smoke dampers of HVAC in the Technical Standard for Smoke Management Systems in Buildings(GB 51251 - 2017),Code for Fire Protection Design of Buildings(GB 50016 - 2014)(2018 Version),Code for Design of Automatic Fire Alarm System(GB 50116 - 2013),Standard for Electrical Design of Civil Buildings(GB 51348 - 2019)
are sorted out and compared to analyze the types,functions,setting positions,signal feedback,and control requirements of various dampers and their relationship with the automatic fire alarm system.
Key words:fire damper;smoke exhaust fire damper;smoke exhaust damper;smoke management;signal feedback;linkage control;input and output module;automatic fire alarm system
摘 要:整理比较GB 51251 - 2017《建筑防烟排烟系统技术标准》、GB 50016 - 2014《建筑设计防火规范》(2018年版)、GB 50116 - 2013《火灾自动报警系统设计规范》、GB 51348 - 2019《民用建筑电气设计标准》对暖通专业各类防火阀、排烟防火阀、排烟阀等的相关规定,分析各类阀的类别、作用、设置位置、信号反馈、控制要求及其与火灾自动报警系统的关联等问题。
关键词:防火阀;排烟防火阀;排烟阀;防排烟;信号反馈;联动控制;输入输出模块;火灾自动报警系统