GB 50016 - 2014中柴油发电机房设置场所要求小议
李炎斌(深圳市华阳国际工程设计股份有限公司,广东省深圳市 518032)
Discussion on Requirements for Setting Place of Diesel Generator Room in GB 50016 - 2014
LI Yanbin(CAPOL International & Associates Group,Shenzhen 518032,Guangdong Province,China)
Abstract: According to the requirements for the layout location of diesel generator room in the project drawing review,in combination with the interpretation of corresponding terms in the Fire Protection Law of the People’s Republic of China,this paper analyzes the rationality and adaptability of the drawing review opinions and the requirements of relevant normative provisions,and puts forward that the normative standard terms shall be consistent with the terms of legal provisions as the basis.
Key words:Code for Fire Protection Design of Buildings(GB 50016 - 2014);Fire Protection Law of the People’s Republic of China;location of diesel generator room;people gathering place;fire drawing review opinions;rationality;adaptability;explosion hazard
摘 要:根据项目审图中关于柴油发电机房布置位置的要求,结合《中华人民共和国消防法》中相应名词解释,分析审图意见及相关规范条文要求的合理性及适应性,并提出规范标准名词应与作为基础的法律条文名词保持一致。
关键词:GB 50016 - 2014《建筑防火设计规范》;《中华人民共和国消防法》;柴油发电机房位置;人员聚集场所;消防审图意见;合理性;适应性;爆炸危险性
中图分类号:TU852 文献标识码:A
doi:10.3969 / j. issn.1003 - 8493.2022.01.002