综合交通枢纽工程供配电系统负荷转移方案研究

来源于: 发表时间:2022-03-28 17:03 编辑:fzy

 

综合交通枢纽工程供配电系统负荷转移方案研究

张振宇(北京城建设计发展集团股份有限公司,北京市 100037

Study on Load Transfer Scheme for Power Supply and Distribution System

of Integrated Transportation Hub Project

ZHANG Zhenyu(Beijing Urban Construction Design & Development Group

Co.,Limited,Beijing 100037China)

 

 

AbstractIn light of the significant power consumption with the integrated transportation hub and the high proportion of Class I and Class II load,the rationality of power supply and distribution scheme directly affects the reliability of power supply and the convenience for emergency dispatching,as well as the characteristics of construction investment at the initial phasebased on the available load data of some practical engineering cases,this paper analyzes and investigates the merits and demerits of the conventional power supply and distribution system design scheme that introduces 4-way 10kV power supply and sets 2 switching stations. In view of the gaps with the conventional design scheme,this paper proposes the load transfer technical scheme with threeway power supply and four buses.

Key wordsintegrated transportation hub;power supply and distribution system;power supply capacity;reliability;load transfer;diesel generator;switching station;threeway power supply and four buses

 

摘 要:结合综合交通枢纽用电量大,一、二级负荷占比高,供配电方案的合理性直接影响供电的可靠性、紧急调度方便性,同时影响初期建设投资的特点,以实际工程案例负荷资料为基础,对传统供配电系统设计方案中外引410 kV电源、设置2个开闭所方案优缺点进行分析研究。针对传统设计方案存在的不足,提出三电源四母线的负荷转移技术方案。

关键词:综合交通枢纽;供配电系统;供电能力;可靠性;负荷转移;柴油发电机;开闭所;三电源四母线