某国际品牌仓储基地供电方案设计
赵灵芝(华东建筑设计研究院有限公司,上海市 200002)
Power Supply Scheme Design of Storage Base for an International Brand
ZHAO Lingzhi(East China Architectural Design & Research Institute Co.,Ltd.,Shanghai 200002,China)
Abstract:Combined with the actual situation of the project and the problems in the design process,this paper does not only design three different power supply schemes for an international brand storage base,but also introduces and analyzes the power consumption capacity and machine room layout of each scheme as well as makes a comprehensive comparison from the aspects including technology and economy,and determines the scheme selection to meet the actual power demand of the project.
Key words:storage base;load division;electric consumption index;machine room layout;power supply and distribution design;load calculation;scheme selection;technical and economic feasibility
摘 要:结合项目实际情况和设计过程中出现的问题,为某国际品牌仓储基地设计了3种不同供电方案,介绍、分析各个方案的用电容量及机房布置,并从技术性、经济性等方面进行综合比较,确定方案选择,以满足项目的实际用电需求。
关键词:仓储基地;负荷划分;用电指标;机房布置;供配电设计;负荷计算;方案选择;技术经济性
中图分类号:TU852 文献标识码:A
doi:10.3969 / j. issn.1003 - 8493.2022.06.008