徐建兵 郭 东 李 慧 郑 宇(中国建筑西南设计研究院有限公司,成都市 610042)
张 晓(中海佳隆成都房地产开发有限公司,成都市 610042)
Research on Power Conversion Control Strategy of Super High‑rise Building
XU Jianbing GUO Dong LI Hui ZHENG Yu
(China Southwest Architectural Design and Research Institute Corp. Ltd,Chengdu 610042,China)
ZHANG Xiao(Zhonghai Jialong Chengdu Real Estate Development Co.,Ltd,Chengdu 610042,China)
Abstract:Combined with the characteristics of power supply and distribution system of super high‑rise buildings and the requirements of relevant codes,a power supply and distribution system architecture considering reliability and economy is proposed. Through the analysis and research on the functional characteristics,mode setting and coordination between upper and lower levels of power conversion devices at all levels and combined with practical engineering case,the control strategy of MV priority and secondary coordination that meets both codes and operational requirements is put forward.
Key words:super high‑rise building;power supply and distribution system;emergency power supply;power conversion;radial structure;main station‑substation structure;spare to each other;automatic charge and automatic recovery
摘 要:结合超高层建筑供配电系统的特点及相关规范要求,提出兼顾可靠性和经济性的供配电系统架构。通过对各级电源转换装置功能特点、模式设定、上下级配合等方面的分析研究,结合实际工程案例,提出既满足规范又符合营运需求的中压优先、二级配合控制策略。
关键词:超高层建筑;供配电系统;应急电源;电源转换;放射式结构;主站-分站结构;互为备用;自投自复
中图分类号:TU852 文献标识码:A
doi:10.3969 / j. issn.1003 - 8493.2022.12.001