配光曲线与马道位置对体育馆照明质量的影响分析
王小虎 金 超 孙开赜 严雪祯(云南省设计院集团有限公司,昆明市 650228)
Analysis of Influence of Light Distribution Curve and Catwalk Position
on Gymnasium Lighting Quality
WANG Xiaohu JIN Chao SUN Kaize YAN Xuezhen
(Yunnan Design Institute Group Co.,Ltd.,Kunming 650228,China)
Abstract:Taking basketball gymnasium as an example, this paper uses DIAlux simulation software to conduct a simulation analysis of the gymnasium lighting quality under different light distribution curves and different catwalk positions,including average horizontal illuminance,average vertical illuminance,horizontal uniformity ratio of illuminance and vertical uniformity ratio of illuminance;studies on the influence of light distribution curves and catwalk positions on the lighting quality,and draws relevant conclusions.
Key words:gymnasium;DIAlux;luminaire light distribution curve;projection distance;catwalk installation position;simulation;illuminance calculation;illumination quality
摘 要:以篮球馆为例,利用DIAlux仿真软件分别对体育馆中不同配光曲线与不同马道位置下的照明质量进行仿真分析,包括平均水平照度、平均垂直照度、水平照度均匀度和垂直照度均匀度,研究配光曲线与马道位置对照明质量的影响并得出相关结论。
关键词:体育馆;DIAlux;灯具配光曲线;投射距离;马道安装位置;仿真;照度计算;照明质量
中图分类号:TU 245.2 文献标识码:A
doi:10.3969 / j. issn.1003 - 8493.2023.01.008