埃及轻轨牵引供电系统避雷器选型与配置探讨

来源于: 发表时间:2023-03-31 15:03 编辑:fzy

 

埃及轻轨牵引供电系统避雷器选型与配置探讨

代文平    毅(四川艾德瑞电气有限公司,成都市 610031

      琨(中铁二院工程集团有限责任公司,成都市 610031

Discussion on the Model Selection and Configuration of the Surge Arrester for the Traction Power Supply System of Egypt Light Rail Transit

DAI Wenping HE YiSichuan Edri EDRI Co.,Ltd.,Chengdu 610031China

YIN Lei XIAO KunChina Railway Eryuan Engineering Group Co.,Ltd.,Chengdu 610031China

 

 

AbstractThis paper describes the application of surge arrests in the traction power supply system of the electrified railway. Based on the calculation principle of key parameters of a surge arrester specified in IEC standards,such as rated voltage,continuous operating voltage and nominal discharge current as well as the traction power supply system used in Egypt Light Rail Transit,the calculation for parameter selection of 220 kV,27.5 kV and 20 kV surge arresters was analyzed,the configuration of arresters in the traction power supply system of Egypt Light Rail Transit was summarized and sorted out,and solutions to the O&M difficulties of arresters used in the Project were provided,showing a good demonstration of a project combining the local characteristics of countries of the“Belt and Road Initiative”with Chinese characteristics and making Chinese wisdom,Chinese solutions and Chinese equipment“Go Out”.

Key wordsmodel selection of the surge arrester;rated voltage;continuous operating voltage;nominal discharge current;nominal voltage of the system;maximum operating voltage of the system;traction power supply system of the light rail transit;insulation coordination of the substation

摘 要:介绍避雷器在电气化铁道牵引供电系统中的应用,根据IEC标准给出避雷器的额定电压、持续运行电压、标称放电电流关键参数的计算原则,结合埃及轻轨牵引供电系统分析了220 kV27.5 kV20 kV避雷器的参数选型计算,总结梳理埃及轻轨牵引供电系统的避雷器配置,针对项目避雷器运维难点给出解决措施,实现了兼具一带一路国家本土特点和中国特色的中国智慧、中国方案、中国装备走出去的良好示范。

关键词:避雷器选型;额定电压;持续运行电压;标称放电电流;系统标称电压;系统最高工作电压;轻轨牵引供电系统;变电所绝缘配合

中图分类号:TU895                   文献标识码:A

doi10.3969 / j. issn.1003 8493.2023.03.007