账号:
密码:
    QQ登录
建筑电气
当前位置:首页 >> 建筑电气杂志 >> 2023年第3期(总第304期)

飞轮和化学储能UPS在数据中心的应用对比分析

来源于: 发表时间:2023-03-31 16:03 编辑:fzy

飞轮和化学储能UPS在数据中心的应用对比分析

李国会 张晶 刘明 张凯力 孙思宇(中国建筑西南设计研究院有限公司,成都市 610042

Comparative Analysis of Application of Flywheel and Chemical Energy Storage UPS in Data Center

LI Guohui ZHANG Jing LIU Ming ZHANG Kaili SUN SiyuChina Southwest Architectural Design and Research Institute Corp. Ltd,Chengdu 610042China

 

 

AbstractThere are design cases for UPS in the form of lithium battery energy storage in Level A data centers,and flywheel energy storage has attracted the attention of some constructors as a new form of energy storage. Taking an actual engineering parameter as an example,this paper analyzes the characteristics of the two forms of energy storage based on the perspective of backup time,service life,cost,power supply reliability and occupied civil construction area attracting the attention of the constructors. The results show that the flywheel energy storage mode is not suitable as a form of UPS energy storage in Level A data centers at this stage,but can theoretically be used in Level C data centers.

Key wordslithium battery;flywheel energy storage;Level A data centers;UPS;service life;cost;power supply reliability;occupied civil construction area

 

摘 要:锂电池储能形式UPSA级数据中心已有设计案例,飞轮储能作为新出现的储能形式受到了部分建设方的关注。本文以某实际工程参数为例,基于建设方所关注的后备时间、使用寿命情况、造价、供电可靠性、占用土建面积等角度来分析两种储能形式的特点。结果显示,在现阶段飞轮储能模式暂不适合作为A级数据中心UPS储能形式,理论上可以用于C级数据中心。

关键词:锂电池;飞轮储能;A级数据中心;UPS;寿命;造价;供电可靠性;占用土建面积

中图分类号:TU852                   文献标识码:A

doi10.3969 / j. issn.1003 8493.2023.03.002

相关信息:

  • 推荐文章

  • 热门文章