建筑电气
当前位置:首页 >> 建筑电气杂志 >> 2024年第2期(总第315期)

消防疏散照明中的灯具布置策略研究

来源于: 发表时间:2024-03-01 16:03 编辑:fzy

 

昊(北京市建筑设计研究院有限公司,北京市 100045

Research on the Strategy for Luminaire Arrangement in Fire Evacuation Lighting

YAN HaoBeijing Institute of Architectural Design Co.,Ltd.,Beijing 100045China

 

 

AbstractThe basis for the selection of luminaires in fire evacuation lighting is introduced,the selection,installation height,and arrangement spacing of light sources in fire evacuation lighting are analyzed,and control light source is defined. Besides,the calculation formula for the minimum horizontal illuminance on the ground for different installation heights and spacing is derived from such light source parameters,and thus appropriate installation spacing for emergency lighting luminaires under different standards for evacuation illuminance are given. Meanwhile,a brief discussion is conducted on the illuminance uniformity of evacuation lighting,and the number of luminaires provided in the emergency lighting circuit is analyzed based on battery characteristics and the voltage drop of DC power supply.

Key wordsfire evacuation lighting;fire emergency lighting luminaire;luminaire arrangement;distribution of luminous intensity;illuminance calculation;illuminance uniformity;storage battery;voltage drop

 

摘 要:简述消防疏散照明中的灯具选择依据,并对疏散照明中的光源选择、安装高度、布置间距进行分析;定义疏散照明控制光源,并在此光源参数下推导出不同安装高度和间距下的地面最低水平照度计算公式,进而给出不同疏散照度标准下适宜的应急照明灯具安装间距。同时对疏散照明中的照度均匀度进行简要探讨,并结合蓄电池特性和直流电源电压降,分析应急照明回路中的灯具配接数量。

关键词:消防疏散照明;消防应急照明灯具;灯具布置;光强分布;照度计算;照度均匀度;蓄电池;电压降

中图分类号:TU113.6 + 4         文献标识码:A

doi10.3969 / j. issn.1003 8493.2024.02.009