对《消防设施通用规范》部分条文的理解

来源于: 发表时间:2024-06-29 15:06 编辑:fzy

 

余悦兰(华侨大学建筑设计院(泉州)有限责任公司,福建省泉州市 362021

Understanding of Some Articles in the General Code for Fire Protection Facilities

YU Yuelan(Architectural Design InstituteHuaqiao University(Quanzhou)

Co.,Ltd.,Quanzhou 362021Fujian Provice,China)

 

 

AbstractThe“and”logic,alarm area,fire control room setting,combustible gas detection and alarm system and wiring design of automatic fire alarm system are discussed based on some articles of General Code for Fire Protection Facilities(GB 55036 - 2022). For example,

how to compare the scheme of setting up the fire control room when it is necessary to design the renovation and expansion project of the automatic fire alarm system;how to execute the linkage operation including starting the fire sound and light alarm in the protected area,automatically closing the flammable gas valve and opening the emergency exhaust fan after the combustible gas alarm controller sends an alarm signal.

Key wordsautomatic fire alarm system;“and”logic;alarm area;fire control room;combustible gas detection and alarm system;wiring;alarm;linkage

 

摘 要:结合GB 55036 - 2022《消防设施通用规范》的部分条文探讨火灾自动报警系统的逻辑﹑报警区域﹑消防控制室设置﹑可燃气体探测报警系统及布线设计等方面的问题,如:需要设计火灾自动报警系统的改﹑扩建项目,如何对消防控制室的设置方式进行方案比选;可燃气体报警控制器发出报警信号后,如何执行包括启动保护区域的火灾声光警报器﹑自动关闭可燃气体阀门并打开事故排风机的联动操作等。

关键词:火灾自动报警系统;逻辑;报警区域;消防控制室;可燃气体探测报警系统;布线;报警;联动