411.4.1 In TN systems the integrity of the earthing of the installation depends on the reliable and effective connection of the PEN or PE conductors to earth. Where the earthing is provided from a public or other supply system, compliance with the necessary conditions
external to the installation is the responsibility of the supply network operator.
NOTE 1 Examples of conditions include:
− the PEN is connected to earth at a number of points and is installed in such a way as to minimize the risk of a break in the PEN conductor;
− RB/RE ≤ 50/(Uo-50)
where
RB is the earth electrode resistance, in ohms, of all earth electrodes in parallel;
RE is the minimum contact resistance with earth, in ohms, of extraneous-conductive-parts not connected to a protective conductor, through which a fault between line and earth may occur;
Uo is the nominal a.c. r.m.s. voltage to earth, in volts.
NOTE 2 In Germany compliance with condition RB/RE ≤ 50/(Uo-50) is compulsory for the supply network operator.
NOTE:In Germany,condition RB/RE ≤ 50/(Uo-50)——the supply network operator:compulsory! |
|