6. ESCAPE ROUTE LIGHTING
6.1 For escape routes up to 2 m in width, the horizontal illuminance on the floor along the
centre line of an escape route shall not be less than 1 lx and the central band
consisting of not less than half of the width of the route shall be illuminated to a
minimum of 50 % of that value.
NOTE: Wider escape routes can be treated as a number of 2 m wide strips or be
provided with open area (anti-panic) lighting.
6.2 The ratio of the maximum to the minimum illuminance along the centre line of the
escape route shall not be greater than 40 : 1.
NOTE: To prove the ratio a grid system should be used according to CIE S 015, chap.
4.3.3. |
|