Regulation 434.5.2 requires that where a protective device is provided for fault current
protection only (and not overload protection), it shall be ensured that the
disconnection time t is such that the live conductor temperature shall not exceed
those temperatures given in Table 43.1. The formula quoted is:
where:
t = k2 S2/I2
t is the duration in seconds
S is the cross sectional area of conductor in mm2
I is the effective fault current, in amperes, expressed for a.c. as the rms value, due account being
taken of the current-limiting effect of the circuit impedances
k is a factor taking account of the resistivity, temperature coefficient and heat capacity of the
conductor material, and the appropriate initial and final temperatures. The values of k can be
obtained from manufacturers.
This equation applies to the live conductors. The temperature corrections to be made
will be as for shock protection in paragraph 5.3.1, i.e. to working temperature for
devices in Appendix 3 of BS 7671 (column 3 of Table 5.1) and to average of
working temperature and limiting final temperature for other devices. |