433.3.3 Cases where omission of devices for overload protection shall be considered
for safety reasons
The omission of devices for protection against overload is permitted for circuits supplying
current-using equipment where unexpected disconnection of the circuit could cause danger or
damage. Examples of such cases include:
exciter circuits of rotating machines;
supply circuits of lifting magnets;
secondary circuits of current transformers;
circuits which supply fire extinguishing devices;
circuits supplying safety services (burglar alarm, gas alarms, etc.).
NOTE In such cases, consideration should be given to the provision of an overload alarm. |
|